DARUSA
- New York City
Can you have a 277 volt outlet in the residential corridor?
They don't make 277 standard outlets that I am aware of.
You can use a commercial outlet, though. Not a 20 amp on a 15 amp circuit though.
By standard I mean that it would use normal power. Like in a house.
Sounds like he wants to use a 277 volt rated receptacle on a 120/240 system.
We have a building project with dual voltage 120/208 and 277/480 volt .The blue prints shows a 277 outlet in the corridor on a residential section of the building.
Have you read NEC 2008 210.6(A) Occupancy Limitation. It's my understanding that 'dwelling units' aka residential cannot have cord and plug or luminaires connected loads in excess of 120 volts.![]()
210.6 Branch-Circuit Voltage Limitations.
The nominal voltage of branch circuits shall not exceed the values permitted by 210.6(A) through (E).
(A) Occupancy Limitation. In dwelling units and guest rooms or guest suites of hotels, motels, and similar occupancies, the voltage shall not exceed 120 volts, nominal, between conductors that supply the terminals of the following: See related Staff Note
(1) Luminaires
(2) Cord-and-plug-connected loads 1440 volt-amperes, nominal, or less or less than ? hp
Does it include corridors?
No, it does not include corridors, hallways and such that are external to the respective unit, room, or suite.210.6 Branch-Circuit Voltage Limitations.
(1) Luminaires
Has nothing to do with the corridor being in a residential or commercial "section". For instance, in a hotel, the entire building is commercial.The question to ask is the 'corridor' part of the residential section, or is part of the commercial section?? Will the tenants/persons from the residential be using this?? If it's part of the residential section or if the tenants(that live in the residential section for their purposes) are using it, then I say its a code violation. What do your prints show again?
No, it does noy include corridors, hallways and such that are external to the respective unit, room, or suite.
What about 210.6 C Does it allow the installation?