277 volt outlet on a residential
They don't make 277 standard outlets that I am aware of.
You can use a commercial outlet, though. Not a 20 amp on a 15 amp circuit though.
what do you mean by 'standard outlet' vs 'commercial outlet'?
dont know if this is what you were thinking of, but there is a 15 amp 277v duplex receptacle. NEMA 7-15 is the designation for 15amp 277v.
Sounds like he wants to use a 277 volt rated receptacle on a 120/240 system.
Have you read NEC 2008 210.6(A) Occupancy Limitation. It's my understanding that 'dwelling units' aka residential cannot have cord and plug or luminaires connected loads in excess of 120 volts. ;)
210.6 Branch-Circuit Voltage Limitations.
The nominal voltage of branch circuits shall not exceed the values permitted by 210.6(A) through (E).
(A) Occupancy Limitation. In dwelling units and guest rooms or guest suites of hotels, motels, and similar occupancies, the voltage shall not exceed 120 volts, nominal, between conductors that supply the terminals of the following: See related Staff Note
(1) Luminaires
(2) Cord-and-plug-connected loads 1440 volt-amperes, nominal, or less or less than ? hp
Does it include corridors?
(1) Luminaires
The question to ask is the 'corridor' part of the residential section, or is part of the commercial section?? Will the tenants/persons from the residential be using this?? If it's part of the residential section or if the tenants(that live in the residential section for their purposes) are using it, then I say its a code violation. What do your prints show again?
(1) Luminaires
No, it does not include corridors, hallways and such that are external to the respective unit, room, or suite.
Has nothing to do with the corridor being in a residential or commercial "section". For instance, in a hotel, the entire building is commercial.
What matters is to whom it is accessible. If accessible by residents or guests of more than one dwelling unit, guest room or suite, or by the general public, the requirement is relinquished.
No, it does noy include corridors, hallways and such that are external to the respective unit, room, or suite.
I'm sorry I have to disagree. If the 'corridor' is part of the residential section aka 'dwelling unit' then it is including. To me a corridor is just another name for a hallway. We don't break up 'dwelling unit/residential buildings to exclude hallways/corridors. The term 'dwelling unit' is all encompasing of hallways/corridors,sleeping, eating etc..
To install that 277 outlet in the residential section is a code violation. And no, (C) does not give any exception for doing this in dwelling unit.