Panel Schedules
Karl H
San Diego,CA
If you have a 9KW three phase load @208 (PF isn't known).
To find VA, wouldn't it be 9000/360=25x208=5200.
So phase A=5200
B=5200
c=5200
Am I missing something here? I'm really drawing a blank.:-?
It seesm to me without knowing the power factor or any data on the type of load yiu simply have to say, k*w is basically k*v*a.
You have a 9kw load on 208 volts it would be 300 kw per pahse and a 25 amp load.
Maybe I'm missing something
You cannot calculate the KVA with the information given. Both calculations so far assume a PF of 1. The formula would be:
W / PF = VA
9000W / 1 (PF) = 9000 VA
Now assume a PF of .5
9000W / .5 (PF) = 18000 VA
Voltage does not need to be known.
Hope this helps.
So phase A=5200
B=5200
c=5200
9000/360=25A X 120 ( leg to ground)=3000 VA per phase
(not leg to leg)