If a 25 hp motor is running at 40% of its flc is it time to resize the motor for better effiency, if possible ? The motor is running continuous most of the day. Motor is 480 volt and no vfd or soft starts.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
If a 25 hp motor is running at 40% of its flc is it time to resize the motor for better effiency, if possible ? The motor is running continuous most of the day. Motor is 480 volt and no vfd or soft starts.

Replacing it with a 10HP motor running at full load might save you 1 or 2 percent of the energy cost, a lot more if your original motor was not a newer energy efficient design and the new one is (will be). If you look at a motor's efficiency rating, it is a curve that peaks at between 75 and 100% of full load and declines slightly starting at (typically) around 50% loading, dropping about 4% between 50% load and 10% load. So depending on your motor's specific curve (they vary), if you are truly at 40% load continuously you may be heading into the lower parts of that efficiency curve. But this must be weighed against the possibility that the original design engineer knew what he/she was doing and considered occasional overloading or acceleration torque into the decision to use a 25HP to begin with. In other words, a 10HP motor that stalls saves you nothing.