Does a seperate disconnect need to be installed near the house (singlewide trailer) or will the main breaker in the panel serve as the disconnecting means ?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Does a seperate disconnect need to be installed near the house (singlewide trailer) or will the main breaker in the panel serve as the disconnecting means ?
I don't do trailers but I am quite certain a separate disco. is needed outside the trailer.
 

Derick

Member
Does a seperate disconnect need to be installed near the house (singlewide trailer) or will the main breaker in the panel serve as the disconnecting means ?

550-11A (singlewide trailer means mobile homes?)
I just looked in NEC could be wrong.We stop at pedestal point and can't do any on mnf.bld
 

jaylectricity

Senior Member
Location
Massachusetts
Occupation
licensed journeyman electrician
You need to be able to disconnect the entire trailer from power from a location in view of the trailer and not more than 30 feet away.
 