091201-0931 EST
steve66:
If I put my test sample of Romex in a 1/2" conduit the capacitance of 25 pfd from hot to EGC when in free space becomes 31 pfd/ft with EGC and conduit connected together. The other conductor is floating. We are not concerned with the capacitance of the conductor I left floating for the reason above. However, if it is also connected to the conduit there is a negligible change, less than 1 pfd.
I roughly agree with your calculation on Xc other than for the use of 1400 ft. Using 700 ft your value would be doubled. This is way above 120/.005 = 24000 ohms.
The Sq-D note is probably a useful value to protect them from a lot of other factors. One of which is the inrush current to this line capacitance when the initial charge is zero and the breaker is turned on at the peak of the voltage waveform. However, I really believe the threshold detector input low pass filter should prevent this problem.