alaskanassassin
Member
- Location
- Fairbanks, Alaska
I have a 1KVA, 480V/120V control transformer and I need to make sure my calculations are correct. I am using 430.3(B). Primary side 1000/480=2.08 amps, 2.08X250%=5.2 amps. Secondary side 1000/120=8.33 amps, 8.33X125%=10.4 amps. Am I doing this right? I plan on using KTK fuses on the primary and using FNM fuses on secondary. What type of fuses do you typically use? Fast or slow acting? Thanks Doug