We have just recently had an arc flash study completed and have been told by the certified NFPA 70 E master trainer that gave us the training that we could no longer open and close breakers in our medium voltage switch gear unless we are suited up for the job, even though the breakers are fully enclosed. We have breakers that are marked category dangerous which means on safe ppe exist to do this work energized. This leads into the question. We have double ended switch gear, each end has a transformer that takes the voltage from 12.47kv to 480 volts and on the primary side of the transfomer. The switches are rated for 600 amps on the transformer rating is 1000kva. I do not want to take out major sections of my plant in order to reset a breaker. The primary knife disconnects are kirk keyed with the main. I am thinking about utilizing a second key so that I can open the knife disconnect, since the primary side of the transformer is category 0 and the secondary side is cat dangerous. I have not been able to find any codes that require the use of kirk keys. I talked with the load switch manufactures and they say I can open and close the switch many times , with no problems. When I talk to the gear manufacture, they tell me they can not recommend bypassing the kirk key system. Ther switch manufacture sold the swith in this case to ABB who then created the assembly. The primary current of the transfomer under full load is less than 100 amps. I am looking for any commnets in regards to the arc flash, opening and closing the knife switch under load and any code requirements for the use of the kirk key system.
Thanks