N ninosparkz Member Dec 1, 2009 #1 Can AC cable penetrate wallboard into plemum ceiling than back into w.b. to avoid box beam?
D dcspector Senior Member Location Burke, Virginia Dec 1, 2009 #3 ninosparkz said: Can AC cable penetrate wallboard into plemum ceiling than back into w.b. to avoid box beam? Click to expand... What type of Plenum? See 300.22
ninosparkz said: Can AC cable penetrate wallboard into plemum ceiling than back into w.b. to avoid box beam? Click to expand... What type of Plenum? See 300.22
raider1 Senior Member Staff member Location Logan, Utah Dec 1, 2009 #4 If you are talking about a suspended ceiling space used to convey return air, then take a look at 300.22(C)(1) for the wiring methods permitted in other spaces used for environmental air. Chris
If you are talking about a suspended ceiling space used to convey return air, then take a look at 300.22(C)(1) for the wiring methods permitted in other spaces used for environmental air. Chris
cowboyjwc Moderator Staff member Location Simi Valley, CA Dec 1, 2009 #5 No matter what wiring method you use you will have to seal the penetrations also. Hey Greg, where ya been?
No matter what wiring method you use you will have to seal the penetrations also. Hey Greg, where ya been?