- Bremerton, Washington
- Master Electrician
I am reviewing plans for a ultra violet water treatment facility. It the typical PLC and equipment cabinets. Voltage is 380/277 and 120/208, about a 500 ampere service. The plans call for a 2 AWG copper EGC to all cabinets and equipment such as motors.
I feel this is excessive, lets use the EGC in the supply circuit to clear a fault and not create a parallel path to lessen the fault current in the supply circuit.
Comments?
It almost seems like it was spec'd from a power plant design. The duct bank is sch 80 PVC with 4,000 psi concrete, #4 rebar around it.
I normally use sch 40 and call it good.
Comments?