We have an application where we are pulling in a starter to supply power to a vfd. The starter has an MCP breaker and solid state overload device. (Prob not code compliant). When we want to start the motor we pull in the starter which then poweres up the vfd and in turn starts to motor up to a set requency.
When we pull in the starter however the solid state overload device is taking it down on a "phase loss". We disabled the phase loss detection and everything works fine. Current is seen on all three legs.
Any ideas what could be causing this phase loss on the relay ahead of the drive? The only thing I can guess is that maybe the drive was set up for single phase.
The only other thing I'd guess would be the internal drive capacitance or harmonics?
When we pull in the starter however the solid state overload device is taking it down on a "phase loss". We disabled the phase loss detection and everything works fine. Current is seen on all three legs.
Any ideas what could be causing this phase loss on the relay ahead of the drive? The only thing I can guess is that maybe the drive was set up for single phase.
The only other thing I'd guess would be the internal drive capacitance or harmonics?