P pepevegac Member Dec 3, 2009 #1 Does anybody knows if there is a code that says you can't install a seal tight 90 on a conduit stub through the roof in order to connect whip into the AC unit. In other words there is a stub trhough the roof with 2 seal tight 90
Does anybody knows if there is a code that says you can't install a seal tight 90 on a conduit stub through the roof in order to connect whip into the AC unit. In other words there is a stub trhough the roof with 2 seal tight 90
raider1 Senior Member Staff member Location Logan, Utah Dec 3, 2009 #3 480sparky said: 300.18 maybe? Click to expand... That would definitely make the OPers installation tough to accomplish. Chris
480sparky said: 300.18 maybe? Click to expand... That would definitely make the OPers installation tough to accomplish. Chris
480sparky Senior Member Location Iowegia Dec 3, 2009 #4 raider1 said: That would definitely make the OPers installation tough to accomplish. Chris Click to expand... I didn't the the NEC was written to make anything easy! (90.1(B) in particular)
raider1 said: That would definitely make the OPers installation tough to accomplish. Chris Click to expand... I didn't the the NEC was written to make anything easy! (90.1(B) in particular)
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Dec 3, 2009 #5 Are either of the connectors concealed ? 350.42 & 356.42.....
raider1 Senior Member Staff member Location Logan, Utah Dec 3, 2009 #6 augie47 said: Are either of the connectors concealed ? 350.42 & 356.42..... Click to expand... Good point. From what I semise from reading the original post the 90s would both be exposed. Chris
augie47 said: Are either of the connectors concealed ? 350.42 & 356.42..... Click to expand... Good point. From what I semise from reading the original post the 90s would both be exposed. Chris