I am not too familiar with residential service installations and was looking at some installation standards provided by the local utility when reading the grounding and bonding it has a diagram that indicates a typical service to the meter 2-phase conductors and a neutral the neutral connect to a set of lugs in the center of the meter and continues to show the load side with the conductors to the main panelboard and the neutral and ground bonded at that point, I understand the bonding at the main thing but here is my question:
The "neutral" to the meter and then to the panelboard is typically bare similar to a concentric neutral on service entrance cabling, but why is the meter itself not grounded? I think of my installation at home where multiple single family homes are served from a single pad mounted xfmr. (in the neighbors back yard) and tapped to serve multiple homes, but what happens to a fault in the meter? The meter would be energized, there would be no OCPD only the wire? Just trying to figure this all out thanks.
The "neutral" to the meter and then to the panelboard is typically bare similar to a concentric neutral on service entrance cabling, but why is the meter itself not grounded? I think of my installation at home where multiple single family homes are served from a single pad mounted xfmr. (in the neighbors back yard) and tapped to serve multiple homes, but what happens to a fault in the meter? The meter would be energized, there would be no OCPD only the wire? Just trying to figure this all out thanks.