Sizing wire for transformers

Status
Not open for further replies.

SOXFAN701

Member
I havent had much experiance with size wire for a transformer on both the primary and secondary side. Could someone please explain the correct way for me to go about that.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Welcome to the Forum...

Same basic steps, calculate the load or proposed load, select the conductor , select the overcurrent device. All this with Art 450 in mind also.
There is one "trick" on transformer secondaries and that is 240.4(F) does not allow "next size up" for transformer secondaries.
Keep in mind Art 450 is for transformer protection, and Art 240 is for the conductors (primarily 240.21)

That help any ?
 