health care facilities
i saw that but where does the code spell out emt. all it says is mechanically protected
Actually it says;
(3) Mechanical Protection of the Emergency System The wiring of the emergency system in hospitals shall be mechanically protected. Where installed as branch circuits in patient care areas, the installation shall comply with the requirements of 517.13(A) and 517.13
(B). The following wiring methods shall be permitted:
(1) Nonflexible metal raceways, Type MI cable, or Schedule 80 rigid nonmetallic conduit. Nonmetallic raceways shall not be used for branch circuits that supply patient care areas.
(2) Where encased in not less than 50 mm (2 in.) of concrete, Schedule 40 rigid nonmetallic conduit, flexible nonmetallic or jacketed metallic raceways, or jacketed metallic cable assemblies listed for installation in concrete. Nonmetallic raceways shall not be used for branch circuits that supply patient care areas.
(3) Listed flexible metal raceways and listed metal sheathed cable assemblies in any of the following:
a. Where used in listed prefabricated medical headwalls
b. In listed office furnishings
c. Where fished into existing walls or ceilings, not otherwise accessible and not subject to physical damage
d. Where necessary for flexible connection to equipment
(4) Flexible power cords of appliances or other utilization equipment connected to the emergency system.
(5) Secondary circuits of Class 2 or Class 3 communication or signaling systems
Roger I was looking at that and MCap HCF could only be used under the subsection of (C)(3)....(3) So one would have to use EMT, IMC or RMC?
That is correct although we do use flexible wiring methods as fixture whips.
Roger
Can the emergency branch circuits serving lighting and rec. in a Cat. lab be ran in MCAP HCF or does it have to be installed in EMT.
Sometimes folks use the term "emergency" quite loosley, so I am just asking...are these truly branch circuits fed from an "emergency" system of life safety and critical branch, or just a standby generator feeding some lights and outlets in a lab?
I would say the OP used "Cat. lab" meaning Catheterization Lab which would be patient care meaning these fixtures and receps would be fed from the Critical Branch not the Equipment Branch.
Roger
As per Rogers Post yes the OP did say mean to say Cath Lab. I know the OP as I inspect his work often and he is a "sharp one" When he called me we were just confused on the actual writting of 517.30. That is why he "Dave" posted this.