aelectricalman
Senior Member
- Location
 - KY
 
Im in a situation where we have a 208/120V panel feed from a 480V system.  This is an old warehouse/factory that was closed many years ago and the equipment we are using was originally in an area for the front offices.  There is the 480V panel and a transformed 208/120V next to it.  The transformer that feeds the 208/120V panel is only rated to supply max 80 amps.  The 208/120V panel fed from it, is fused at 30 amps.  Well, thats a dilema because we are now converting this to a fitness center where 2 tanning beds, 2 saunas and a clothes dryer will be required to run 208V.  There will also be 7- 16 amp treadmills at 120V.  So, at 80% use we are looking at somewhere around 150 amps.  This XFMR also feeds a small panel that was once for "clean power", iso.  Now the issue is that I have to put in a 150 amp disconnect and get 150 amps to the gym in place of the 30 amp.  Next to the transformer in question (80amp), I have an identical transformer with fairly similar impedences.  I dont think we will have any heating issue.  These are older XFMRS, and my concern is that if one fails I might have trouble!  Can I lock out one, when the other trips with a contactor and have a safe assembly.  Are there any other major issues I should look at?  Will I have any tap issues since these are older XFMRs?  Is this a bad idea?
	
		
			
		
		
	
				
			
			