I've been tasked with reducing lighting load at an industrial facility in an effort to reduce utility costs. Rather than hook up a power monitor on each circuit, I've been taking amperage readings using a clamp on ammeter. My theory is a little rusty and I'd like to run my method of calculating load on an unbalanced 3 phase circuit by you guys for accuracy.
Example:
480V 3 phase circuit breaker feeds 11 parking lot fixtures.
Fixtures are 480V single phase L-L (no grounded conductor)
Phase A: 7 amps
Phase B: 7 amps
Phase C: 5.2 amps
Ia + Ib + Ic /3 x 480 X 1.732 = total VA
7 + 7 + 5.2= 19.2 A
19.2 / 3 = 6.4 A
6.4 x 480 x 1.732 = 5.3 kva total
5300 / 11 = 482 VA per fixture
Am I way off base? I ran across a similar post on this forum a while back with a couple different ways of calculating unbalanced loads but can't find the thread using the search function. Any input or alternative calculations would be greatly appreciated.