I have been asked to oversee a project for putting together the electrical design for a new small office/warehouse that will be located in a structure located in our existing industrial facility. The final design will be produced and stamped by and enginner that will review this but in the mean time I want to try to put togther some numbers myself as an exercise in creating a preliminary design.
Does this design need to be stamped by a PE, or can a licenesed electrical contractor put together the design? Not that I would, but could a plant EE as myself finalize this design and submit it for permitting?
I have attached the general layout of the small area I am looking at if anyone cares to comment. I was curious the best approach to take for coming up with the demand and making assumptions for certain things that are shown without great detail yet.
What approach would you take for coming up with these demand calcs and final circuit designs. Here are a couple of my thoughts:
1) There is a bathroom shown which I believe based in the NEC the bathroom needs seperate designated circuits with gfi protection. Does each of the two bathrooms located next to each other need seperate designated circuits?
2) For the lighting should we first determine a number of fixtures, or should a square footage calculation be performed with 3VA per sq ft as I've seen before? How to divide up the circuits. Same with receptacles?
3) There will be some outlets shown for welding receptacles etc.. What is a good rule or procedure for coming up with ratings for these receptacles without knowing the type of equipment that will be plugged in?
4) There is an A/C unit shown as a 3-ton unit. Without knowing the specifics of this unit can a load assumption be made from this size?
Does this design need to be stamped by a PE, or can a licenesed electrical contractor put together the design? Not that I would, but could a plant EE as myself finalize this design and submit it for permitting?
I have attached the general layout of the small area I am looking at if anyone cares to comment. I was curious the best approach to take for coming up with the demand and making assumptions for certain things that are shown without great detail yet.
What approach would you take for coming up with these demand calcs and final circuit designs. Here are a couple of my thoughts:
1) There is a bathroom shown which I believe based in the NEC the bathroom needs seperate designated circuits with gfi protection. Does each of the two bathrooms located next to each other need seperate designated circuits?
2) For the lighting should we first determine a number of fixtures, or should a square footage calculation be performed with 3VA per sq ft as I've seen before? How to divide up the circuits. Same with receptacles?
3) There will be some outlets shown for welding receptacles etc.. What is a good rule or procedure for coming up with ratings for these receptacles without knowing the type of equipment that will be plugged in?
4) There is an A/C unit shown as a 3-ton unit. Without knowing the specifics of this unit can a load assumption be made from this size?