Hi All,
I have a situation on a project that is currently in construction. The design calls out for a new 30kVA step-down transformer (480V - 208/120V) to be installed. The transformer is planned to be installed in an electrical room with a new branch circuit panelboard at 208/120V with a main breaker installed next to the transformer. The transformer is being fed from a 480V distribution board which is located about 50' away. Due to space restrictions within the electrical room, there is a proposed relocation for the branch panelboard. There is space in the adjacent room to place the panelboard, which will be serving said room. Now you have the transformer in the electrical room and the panelboard in the adjacent space over 25' away and the 480V distribution panel in a different room about 50' away.
My question is regarding the required primary and secondary overcurrent protection needed. Based on my review of NEC 240.21 and 450.3, I believe that i would need to provide an overcurrent protection device on the primary side of the transformer AND the secondary side of the transformer within the electrical room. Thus, I would see an enclosed circuit breaker mounted to the left and right of the transformer in the electrical room. Is this correct? I appreciate any help.
I have a situation on a project that is currently in construction. The design calls out for a new 30kVA step-down transformer (480V - 208/120V) to be installed. The transformer is planned to be installed in an electrical room with a new branch circuit panelboard at 208/120V with a main breaker installed next to the transformer. The transformer is being fed from a 480V distribution board which is located about 50' away. Due to space restrictions within the electrical room, there is a proposed relocation for the branch panelboard. There is space in the adjacent room to place the panelboard, which will be serving said room. Now you have the transformer in the electrical room and the panelboard in the adjacent space over 25' away and the 480V distribution panel in a different room about 50' away.
My question is regarding the required primary and secondary overcurrent protection needed. Based on my review of NEC 240.21 and 450.3, I believe that i would need to provide an overcurrent protection device on the primary side of the transformer AND the secondary side of the transformer within the electrical room. Thus, I would see an enclosed circuit breaker mounted to the left and right of the transformer in the electrical room. Is this correct? I appreciate any help.