You cannot share the neutrals you must use a a 3 pole gfci breaker. Three individual devices will not work.with a 3 phase system can you share the same netural with 3 individual GFCIE breakers or do you have to run seperate neturals
Yes, you can use gfci on a mwbc but you cannot use individual sp Gfci snd link them together. It must be a DP or 3P Gfci breaker depending on your MWBCYou can use GFIs on a MWBC. They only check for leakage on their load side, not line. Or am I wrong?
Good point I was thinking eric was asking about line side.You can supply GFCI receptacles from a MWBC.
But if you do, you cannot share the neutral if there's any downstream protected circuits.
I did not say you could.
My post is accurate as written.
I was just adding to it for the enlightenment of others.
Just curious...what does the E at the end of GFCIE stand for?
I feel lighter already.![]()
Only at (or beyond) the load end of the MWBC, where it becomes three separate 2-wire circuits.Would it work if a GFCIE device was used as apposed to a breaker
Equipment?Just curious...what does the E at the end of GFCIE stand for?