Fulthrotl
~Autocorrect is My Worst Enema.~
- E
house, circa 1936 ish. hybrid k&t, ungrounded romex.
looks to be remodeled about 20 years ago, by the panel on
the back of the house. 100 amp service. maybe 1,200 sq. ft.
maybe.
house appears to have had extensive "loving hands of home"
work done. grounded decora devices installed in ungrounded
system.
central heating and AC, maybe 5-8 years old.
now, the complaint by the realtor trying to get this to
fly on a short sale, before foreclosure on jan. 01:
everything works "fine" until you turn off the AC, and then
the lights go off. turn the AC back on, and the lights come on.
AC is carrier unit, with honeywell low voltage controller. vanilla
installation, appears professionally done.
turning on the heater doesn't light the lights. only the AC turned
on will light the lights, and according to the homeowner....
"it wasn't a problem in the summer, but now that it is winter, we
would like the lights to work with the heater as well. is that hard
to do? is it expensive?
honest to god, it was so funny, i had to take a video with my
cellphone of me turning on and off the t stat, and the hall light
going on and off.
supplemental information:
in addition to half the lights going on and off, half the plugs do the
same thing, controlled by the t stat heating/cooling switch on the
honeywell stat. but only with the AC, so this must be someone's
"summer home".
when the "switched" plugs are on, plugging in an ideal suretest,
give a voltage drop, at 15 amps, of 38%, with 71 volts rms being
available at a 15 amp load.
ok, all of you gifts to the electrical industry.... what is the problem?