The way i read it, the disconnecting means must have a rating of 115% of the nameplate rated load current or branch circuit selection current, which in your case is 27 amps (in my opinion). In your situation, I don't know the "rated load current", but since the branch circuit current takes us beyond 30 amps and the next level is 60, I would think you would be covered.
The exception might let you use the 30amp if it has a high enough horsepower rating, but as you can see from 440.12(A)(3) making that determination is a tedious procedure, but a qucik look at that data looks like the switch would need a 5HP rating to qualify.