Per 110.26(A) I am reading that a disconnect that is factory mounted to the AHU still requires the working clearance as stated in 110.26(A).
I wrote up an electrical contractor at a site I walked. The Electrical contractor then wrote an RFI to the Engineer and the engineer said the installation is acceptable per the NEC (But did not give a section).
The clearance currently is 30" and the door opens to about 80 degrees.
Let me know your thoughts on this installation.