I have working with a 4.16kV wound rotor motor with the rotor connected through slip rings to a rheostat during starting. Obviously after the motor has started the leads coming from the rotor are shorted together in the rheostat.
My question is after the rotor leads are shorted together is there still voltage and current on these leads. My question regarding the voltage is that yes there is a voltage (referenced to ground) on these leads because there is still a voltage on the rotor proportional to the stator voltage, slip, and transformation ratio "a" between the stator and rotor.
Now what about current. I know in a squierel cage induction motor there is current circulating in the rotor as a result of the induced voltage in the rotor and the fact that the rotor is shorted on both ends. I'm not exactly how this current interacts for the three phases because I guess the rotor cant be viewed simply as three different phases but rather as all three phase voltages and currents somehow interacting on a single rotor surface. How do the different phases interact with one another if it is one surface and not broken into the different phases?
So would the same apply on the cables between the rotor slip rings and rheostat when they are shorted. Can these be viewed as three different phases somehow having current circulating on them? For the slip ring connections tapped off of the rotor, are they somehow tapped off of seperate phases or sections of the rotor or are they all tapped off of essentially the same rotor surface but just termed the "a, b, and c" rotor phases?