And only for those service conductors that installed in open trenches. Service conductors installed using directional boring do not require the warning tape.300.5(D)(3). This section only applies to service conductors.
Chris
Cool so this is the only sinario where warnig tape applies?
There may be job site specifications that require it.
Agreed, I have done quite a few projects that had specs that required warning tape to be installed on all buried raceways and cables.
Chris
And if it isn't required you could open up your check book, very large expense there, and buy a roll of the tape. If you happened to be next guy digging through that area I bet you would appreciate some tape.
I have no words to express my disappointment for anyone who is too cheap to install warning tape. (Well, to be truthful, I actually do have words, but they would probably be deleted by a moderator. )
300.5 (D) (3) says u/g service conductors that are 18" deep or more and not encased in concrete need the tape. It doesn't mention raceways. I think it's required raceway or not. However,here in S. Fla., FP&L supplies the conduit and pulls the wire. Utilities aren't mandated to follow the code, so the tape wouldn't be required.