Corrosion Protection or not?

Status
Not open for further replies.

Red Wiggler

Senior Member
I hate the Code book sometimes...

I will ask the Authority having Jurisdiction.

344-10 B (1)

(1) Galvanized Steel, Stainless Steel, and Red Brass RMC, Elbows, Couplings, and
Fittings. Galvanized steel, stainless steel, and red brass RMC elbows, couplings, and fittings
shall be permitted to be installed in concrete, in direct contact with the earth, or in areas subject
to severe corrosive influences where protected by corrosion protection and judged suitable for
the condition.


300-6 A (3)
(3) In Concrete or in Direct Contact with the Earth. Ferrous metal raceways, cable armor,
boxes, cable sheathing, cabinets, elbows, couplings, nipples, fittings, supports, and support
hardware shall be permitted to be installed in concrete or in direct contact with the earth, or in
areas subject to severe corrosive influences where made of material approved for the condition,
or where provided with corrosion protection approved for the condition.
Where ferrous or nonferrous metal conduit has corrosion protection and is judged suitable for
the condition, it may be installed in concrete, in contact with the earth, or in areas exposed to
severe corrosive influence. Special precautions are normally necessary for installing
aluminum conduits in concrete and specific approval by the authority having jurisdiction may
be necessary.
Metal raceways installed in the earth can be coated with an asphalt compound, plastic sheath,
or other equivalent protection to help prevent deterioration. Also, metallic raceways are
available with a bonded PVC coating.
[SIZE="5"]Galvanized rigid steel conduit and steel intermediate metal conduit do not generally require
supplementary corrosion protection.[/SIZE]
 

Red Wiggler

Senior Member
Sorry for the Yellow at the bottom

Sorry for the Yellow at the bottom

Sorry for the Yellow at the bottom of the Previous thread. The last statement should read as follows...

Galvanized rigid steel conduit and steel intermediate metal conduit do not generally require
supplementary corrosion protection.


My question is...

Do most of you use some sort of corrosion protection on your GRC that is run in the ground, or concrete?
 

benaround

Senior Member
Location
Arizona
Here in Az. corrosion protection is required. Normally, 20mil tape half lapped is good. If your

soil is real corrosive the GRC won't last long without it.
 