There is another consideration, depending on the seismic zone that you are in. In seismic design categories D, E, and F, ASCE 7 which is referenced by the IBC requires among other things:
"Except where rigid braces are used to limit lateral deflections, sprinkler heads and other penetrations shall have a 2 in. over size ring, sleeve, or adapter through the ceiling tile to allow for free movement of at least 1 in. in all horizontal directions." (ASCE 7, 9.6.2.6.2.2 e.)
This is to allow for side to side movement of the ceiling grid in a earthquake. I think the EMT might be considered to be an "other penetration". In my area at least, rigid braces are not typically used.