Tap rule

Status
Not open for further replies.

triplex15

Member
Location
Virginia
Is it possible to tap and existing 50amp 240 volt circuit to install a 30amp circuit 240 v for a small oven and then tap one leg for 120v microwave circuit. I was trying to clearly understand 210.19 (3) exception #1. Thanks
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Loads permitting, you can tap the 50 amp circuit as desired and feed an overcurrent protective device. 210.19(A)(3) refers to specific appliances
that can be tapped from a 50 amp branch circuit without additional overcurrent protection. I don't see the microwave fitting into the allowable appliances. From the info given, the oven is questionable.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
You could always try to find a place to install a small panel, making the existing cable a feeder (if it's 4-wire), and feed each load from that.
 