shedule 40 PVC

Status
Not open for further replies.

jsartain

Member
Does anyone know what the maximum voltage between conductors allowed to run surface mounted in schedule 40 PVC conduit is?
 
I can't locate a NEC limit. 300.37 allows RNMC above 600 volts, and 328.10 allows MV cable up to 35,000 volts, and I see no limit in Art 352.
What voltage are you thinking of ?
 
The question was posed to me on my journeymans license exam and i cant find it anywhere. I think the options were 150v 250v 300v 600v
 
I can't locate a NEC limit. 300.37 allows RNMC above 600 volts, and 328.10 allows MV cable up to 35,000 volts, and I see no limit in Art 352.
What voltage are you thinking of ?
Its a state code question i got stumped on. my choices were 150v 250v 300v 600v
 
300.2 blankets Chapter 3, UON.


300.2 Limitations.
(A) Voltage. Wiring methods specified in Chapter 3 shall be used for 600 volts, nominal, or less where not specifically limited in some section of Chapter 3. They shall be permitted for over 600 volts, nominal, where specifically permitted elsewhere in this Code.
 