B4T
- Long Island, N.Y.
The feeders where hot to the touch, aluminum. Re torqued two of them but the one in the top right I couldn't move.
The torque specs were still readable?
Tell Al to do it. He'll git 'er done.![]()
I took this picture today responding to a partial power call. Although this had nothing to do with the problem, its typical of what I see with these panels. Notice the bus on the right.
The average home owner knows nothing about electric. Slum lords will not care about safety of tenants. Some simply don't even try to insure these old houses as it is cheap way too tear it down to build new building.
As electricians all we can do is warn them when we see them.
Does that mean I should warn myself about the Zinsco panel in my house? I love that thing. Besides, it would decrease the value of my house if I change it from stock.
BTW, it does trip on over current. It's the short circuit tripping that there are issues with.
I like the stranded wire on the sp20amp at the bottom..just hanging on by a few strands. That lame screw terminal was another fine Zinsco feature, it made barely adequate contact even with solid wire. :roll:
And How does that work with a twin?Get a new breaker and move the tabs on the breaker over to the A bus. You're good to go.
Thomas & Betts and Connecticut Electric make listed Zinsco replacements.
GOOD... lights on.. no smoke
BAD... lights off.. lots of smoke
they are both known for fire hazards but never have i heard them being condemned.
You cannot add a breaker to them, so if additional circuits are needed you must change panel.
No UL listed replacement breakers available.