Wire size for a 500' run
Copper or aluminum?
Voltage & phase?
Overhead (open air), direct burial, or in a raceway?
Any ambient temp issues?
How many conductors?
I would agree with the 1/0 copper, presuming that the "2p" was intended to mean "single phase, two pole."
I would use 2/0, this would ensure max 3% voltage drop. I assumed you were using copper.
I also get 2/0
CM = 2 x K x I x D / VD
CM = 2 x 12.9 x 60 x 500 / 7.2 = 107,500
1/0 = 105,600
2/0 = 133,100
This is assuming that it is actually a 60 amp load not just a 60 amp OCPD. If this is a 60 amp OCPD than the actual load would probably be less than 60 amps. More like 60 X .8 = 48 amp load.
Thanks guys. I found a voltage drop calcualtor in the web. Actually it is a 30A generator pushing power to the 49th flr. I am using 2 AWG copper with a drop of 2.9%. Thanks.
If you're going up the building, wouldn't the voltage get higher as you go? :D
Don't forget if you are using A EGC look at 250.122 (B).
