I believe you are limited to total of 25' feet.
410.137 (c)
“Wired luminaire (fixture) sections are paired, with a ballast(s) supplying a lamp or lamps in both.. For interconnection between paired
units, it shall be permissible to use metric designator 12 (trade size 3/8) flexible metal conduit in lengths not exceeding 7.5m (25 ft), in
conformance with Article 348.” Luminaire wire operating at line voltage, supplying only the ballast(s) of one of the paired luminaires
shall be permitted in the same raceway as the lamp supply wires of the paired luminaires.