I looked at a customer's pool equipment and am not sure I have come to the right conclusion if anybody knows for sure a little help would be nice.
1st off all the pool equipment is fed from a sub-panel that is piped to the main panel and a set of #6THHN conductors are terminated on a 2 pole 60a breaker.
Heat Pump 37a (the largest)
+ 125% = 46.25a (as per 430.24 conductors feeding several motors)
1 1/2hp pump= 7.8a
.5hp blower 120v= 8a
For a grand total of 62.05a which trips the breaker and it should.
If 310.16 says that #6THHN @75Degree's C has an ampacity of 65a and that is not a standand circuit breaker(240.6) can I legally breaker this circuit with a 70a breaker?