quinn77
Senior Member
- Location
- Lake Jackson, TX USA
Recently I was called to a kitchen for fan motors "on fire". When I showed up the fire prot. contractor had already been there to shut them down. The tech. removed on of the motors from the wall mounted exaust hoods outside. He told the owners to call a cert. electrician. The windings had totally melted down, so I investigatd. A 3 ph 208v mbc feeds two 3ph 1HP fan motors with NO THERMAL OVERLOAD protection, just protection for conductors. So I installed 1 40 amp IEC contactor w/ therm. overl. relay at 3.3 FLA in sealed fiberglass enclosures next to the fans. The original electrician( on vacation when problem occured ) recently returned and told owner ( friend of his) that I had sold him something he didn't need. I told him that the N.E.C. required this as with the manufacturer also had instructions on the shroud which read "ELECTRICIAN, IF THREE PHASE, REMOTE SUPPLEMENTAL PROTECTION MUST BE INSTALLED."
Did I overkill this install? Or was my interpretation of the NEC correct?
Did I overkill this install? Or was my interpretation of the NEC correct?