LARRY POTTER
on a service lateral from a 200 disconect on service pole feeding a 100 amp panel in a mobile home what size feeder coductors are required? 100 amp or 200 amp 200 amp (2/0 copper) wont fit under lugs ?
If the panel in the home has 100 amp capability-- 100 amp panel-- then you would only need to run the wire size capable of withstanding the 100 amp panel load.
How far is the disco from the panel in the trailer?
Check out art. 550.32 (A)--must be within 30feet. The reason I was asking was more about VD on the lateral-- say you were 200 feet away then you may have other issues to deal with.not sure exactly how far from disconnect is trailer
is there a code reference for answer i agree but cannot find a section that toatlly agrees
Not sure if you were asking but the appropriate art. for feeders in trailers is 550.33 2008 NECthe disconnect i was aware of
the code section i was refering to was the appropriate one for the feeder conductor