when sizing the GEC for a stand alone generator with OCPD of 800amps. 250.66 states that the GEC should be a 1/0 copper conductor. Can this be connected to ground rod?
 
A grounding electrode that consists of a single ground rod or 2 ground rods never needs to be larger than #6. Take a look at 250.66(A).

Also check out 250.56 if you are using only ground rods for the GES.

Chris
 
As Chris stated the ground rod only needs #6, however the GEC to the water pipes, building steel etc would need to be 1/0.
 
The size of the GEC is determined by the ungrounded conductors, not the OC protection size. 3/0 copper run to a 20 amp beaker would require a 4 AWG copper
 