malachi constant
Senior Member
- Location
- Minneapolis
I am an electrical engineer and recently designed a multifamily dwelling. In meeting with the contractor a question came up about loads related to unit panel sizes. Try to follow me...
Part IV of 220 allows an optional feeder & service load calculation for dwellings. I used 220.82 Dwelling Unit to determine the ampacity of a given unit. All calculated ampacities on this project were between 80A and 96A. So I sized each feeder with #1 AWG conductors, and each panel at 100A.
The contractor thinks this is an issue for some/most of the panels - that each panel needs to be sized at 125% of the calculated load. I don't see that as a requirement in Article 220 or Article 408 Panelboards. Is it a requirement?