ray tieman
Member
we have a 1000 amp main switch board (nema 3r) , in an outdoor concrete enclosed area with no ceiling. The lockable doors open 90-180 degrees,with them open we meet art 110.26 (151-600 volt ) condition 2 , (we have 48" to the deadfront). The nema 3r portion of the enclosure is 9". With the doors closed we have 39" to the concrete wall behind, would the n3r portion count ? The doors have to be open to service.