Hi, I have a resistance spot welder to hook up and need help making sure my calculations are correct.
Welder name plate
250 kva
480 volt
50% duty cycle (.71 630.31(A)(2))
single phase
250000/480x.71=369.8 amps

The welder has a 250 amp thermal overload and the paper work is calling for 400 amp fuses,I think I am missing something or not understanding why there is such a difference between my calculated amp draw and the 250 amp thermal.

Thank's for any help.
 
Because it will take time for the thermal overload to trip as its only "loaded" to 148% of its rating. If the user stays within the duty cycle then the thermal O/L wont trip, as it'll cool down between loadings. If the user goes at it too hard, it'll open. So the fuses protect against catastrophic faults, and the thermal O/L enforces the duty cycle.
 
Hi, I have a resistance spot welder to hook up and need help making sure my calculations are correct.
Welder name plate
250 kva
480 volt
50% duty cycle (.71 630.31(A)(2))
single phase
250000/480x.71=369.8 amps

The welder has a 250 amp thermal overload and the paper work is calling for 400 amp fuses,I think I am missing something or not understanding why there is such a difference between my calculated amp draw and the 250 amp thermal.

Thank's for any help.

Djelectric,
250kVA based on 50% duty cycle is per international standard. When you get max weld current, it has only about 5-6% of duty cycle. That explains why 250A thermal overload used. You also need to check with the thermal overload characteristic.