One of our electrical engineers designed 15KV 750KCMIL AL 133% insulation cable in 5"c duct bank. The diameter of 750KCMIL AL cable is 1.90". So the total cross section area of three cables is around 8.5SQIN. The cross section area of 5"C is around 19.63SQIN. So the percent of cross section of contuit for conductors is around 44%, which is larger than 40%. The design has two 5"C in duct bank, one active and one spare. I am wondering if we can put 2 cables in one conduit and 1 cable in the other in order to meet the code requirement. Any comments is welcome. Thanks.