Bonding, and grounding protection?
Bonding, and grounding protection?
The NEC does require the metal raceways enclosing the grounding conductor to be bonded at both end.
800.100 (A) Grounding Conductor.
(6) Physical Protection. The grounding conductor shall be protected where exposed to physical damage. Where the grounding conductor is run in a metal raceway, both ends of the raceway shall be bonded to the grounding conductor or the same terminal or electrode to which the grounding conductor is connected.
810.58(A) Other Sections.
All grounding conductors for amateur transmitting and receiving stations shall comply with 810.21(A) through (K).
810.21(D) Mechanical Protection.
The grounding conductor shall be protected where exposed to physical damage. Where the grounding conductor is run in a metal raceway, both ends of the raceway shall be bonded to the grounding conductor or to the same terminal or electrode to which the grounding conductor is connected.
820.100 Cable Grounding.
(6) Physical Protection. The grounding conductor shall be protected where exposed to physical damage. Where the grounding conductor is run in a metal raceway, both ends of the raceway shall be bonded to the grounding conductor or the same terminal or electrode to which the grounding conductor is connected.
830.100(A) Grounding Conductor.
(6) Physical Protection. The grounding conductor shall be protected where exposed to physical damage. Where the grounding conductor is run in a metal raceway, both ends of the raceway shall be bonded to the grounding conductor or the same terminal or electrode to which the grounding conductor is connected.