Just curious on how you calculate dc field amps on a motor that hasnt been installed yet? Its a 200 HP 460 volt dc motor FLA is 357 We are testing and recording info on spare motors. Thanks for your help
Just curious on how you calculate dc field amps on a motor that hasnt been installed yet? Its a 200 HP 460 volt dc motor FLA is 357 We are testing and recording info on spare motors. Thanks for your help
You can't usually calculate it. As the others have indicated, you should get the information from the manufacturer. If the motor exists you could maybe measure the resistance of the field winding and work out what it would be if you know the excitation voltage. Bear in mind that what you'd get is the cold field resistance. It may be as much as 20% higher at operating temperature.
My guess, stress guess, based on experience is that your field current will be 15A or less. I have played around with DC shunt and compound wound machines for a few decades. I don't recall any where the shunt field was more than 2-3% of the armature current.
But we all get surprises from time to time. And some of them aren't nice.