[Talking about elecrically operated fans] They are out there. I've seen several in the +1MW range and two in the 300kW range, that have electric drives for the cooling fans.
Having the fan and water pumps driven electrically is common on gensets that are installed in buildings and the radiators are a pipe run away. In these cases the fans and pumps are (when well designed) driven using the power the genset produces, so typically three phase pumps and fans.
One spectacularly terrible design I've seen had five paralled gensets (3 ng cogens on the root, two big standby diesels in the basement) with all the pumps and fans driven off "normal" building power, the idea being that with utility failure the gensets would all start up, syncronise and take the full building load, and the engines would be OK for 30 seconds without coolant flow until the whole thing came on line.
Trouble is, the day the sets didn't want to sync quickly the lack of cooling for some minutes caused all the gensets overtemp protection to operate, causing engine shutdown. So all these gensets were reduced to useless piles of hot metal, and the water-cooled IBM mainframe powered itself off through overtemperature well before the 20 minute UPS battery window expired. No power - no cooling water pumps...
I seem to recall that the problem was that if any of the three cogen sets were running when the utility went out then the syncronisers didn't work. From a cold start with everything stationary (as it always was during commissioning testing) it worked every time...