if i have 8-500 kcmils thw copper conductors entering a commercial steel building then using 250.66 how do i come up with the answer??
my answer is wrong,and trying to figure this out.
8 total conductors
So Let me get this straight,
2 paralleled conduits with 4-500 Kcmil conductors in each conduit.
So according to Table 250.66 Note 1 when more than one set of service entrance conductors are run, you take the equivalent area of the largest service entrance conductor.
So that would be 1000 Kcmil (2 X 500).
Table 250.66 requires the GEC to be sized at 2/0 copper.
Chris
my answer key says 3/0,and here it is so we on same page because i need your help.
minimum required size gec to be bonded to steel building.it is fed with se conductorsof 8-500kcmil copper in parallel per phase.
semantics... I read that to be (8) 500's PER PHASE well over the "over 1100" column in 250.66, thus a 3/0 (maximum required for GEC)
what did you get and how ?
again we are playing "word games". to me "8-500kcmil copper in parallel per phase. " litersally means that EIGHT 500's per phase or (8 x 500) or 4000 kcmil.
I agree, 8 sets of 500 kcmil in parallel equals #3/0 from 250.66.