Welcome to the forum.:)
If you are asking if there is a specific NEC code section that prohibits a feeder from passing through one dwelling unit to another dwelling unit in a multi family dwelling, then the answer is no.
Chris
This is a commercial project. The proposed location of the service disconnect/meter is on the adjoining property. The feeder will cross over the property line from the service panel to a sub-panel on another separate parcel.
Pad transformers are usually in a right-of-way, which is usually within someone's property lines, so it can be unavoidable.
Right-of-way, utility easement, neighborhood covenants and obstruction all come in to play.
I can't think of an NEC problem, but I would not want to create an obstruction on the adjoining property that interfered with normal use and enjoyment of said property.
I would not do it unless there is some understanding already in place and IN WRITING.
You own the airspace above your property. (to a certain point then the FAA would come into play).
I would get an easement.
This is an underground feeder on the load side of the service disconnect. The utility lines would not fall under the NEC.