Here is one for you
A gunite pool that the rear side of the pool is built out of ground approx 4 feet and the contractor wants to put 4 - 12 volt round puck deck lights on the outside wall of this pool, now using a special low voltage transformer you can be within 5 feet of the pool but what about on the pool wall itself.
Below is an article on the 5 foot rule
Section 680.22(B)(4) permits luminaires to be installed within 5 to 10 feet horizontally of the pool?s edge only where a ground-fault circuit interrupter (GFCI) protects the luminaires. Since low-voltage landscape luminaires are supplied by a low-voltage power supply, such as a transformer, providing GFCI protection on the primary side of an isolation transformer will not provide GFCI protection on the secondary side. GFCI devices will not operate at the 15-volts or less supplied by the secondary of the power supply. This leaves only two options: one is to locate all low-voltage landscape lighting at least 10 feet from the pool or fountain edge; or, two, to use a special power supply.
There are low-voltage lighting power units that are marked ?For Use with Submersible Fixtures or Submersible Pumps.? In this case, a special transformer is used that complies with the requirements in 680.23 for underwater luminaires installed below the normal water level of the pool. This transformer is specifically listed for this use and is an isolated winding type transformer with an ungrounded secondary similar to the low-voltage landscape lighting transformer, as required by 411.5(B).