Using the direction conventions given in #18 (important to keep the signs consistent), and the method from #25:
I12* = 600/480@90? = 1.25@-90? = 0 - j1.25 => I12 = 0 + j1.25
I23* = 900/480@-30? = 1.875@30? = 1.6238 + j0.9375 => I23 = 1.6238 - j0.9375
I2 = I23 - I12 = (1.6238 - j0.9375) - (0 + j1.25) = (1.6238 - 0) + j(-0.9375 - 1.25) = 1.6238 - j2.1875 = 2.7243@-53.4132?
You can also solve for the impedances for another method:
R12 = V12^2 / P12 = 480^2 / 600 = 384 ohms
R23 = V23^2 / P23 = 480^2 / 900 = 256 ohms
|I12| = sqrt(P12 / R12) = 1.25 => I12 = 1.25@90?
|I23| = sqrt(P23 / R23) = 1.875 => I23 = 1.875@-30?
I2 = I23 - I12 = 2.7243@-53.4132?
Back to original question ?Calculate the current in the common leg (2)?
1.I believe we should not ignore V31 and I31 in the calculations ? the load is connected to the 3 phase power supply circuit.
2.And finally I see nothing wrong with the following formula for solving this problem: Leg#2=1500w/480v*1.73=1.8A