I am an instructor and have come across an issue with conductor type.
I have always been under the understanding that if a question is asked such as " what is the minimum size conductor needed to supply a load of 87.6 amps" that it is assumed that a THHN copper conductor is used, chosen from the 60 degree column based on 110.14(C)(1) under 100 amps
I was taught this rule 30+ years ago and took it for granted however I have recognized a couple of textbooks that seem to state that unless otherwise noted consider the conductors as THW. Of course this may possibly change some of the way that I teach this, but I was wondering if this was noted in the NEC somewhere or used for uniformity in these tetbooks. I noticed Holt slides show this and an ATP text Electrical Systems based on the 2008 NEC.
Any information is appreciated.
I have always been under the understanding that if a question is asked such as " what is the minimum size conductor needed to supply a load of 87.6 amps" that it is assumed that a THHN copper conductor is used, chosen from the 60 degree column based on 110.14(C)(1) under 100 amps
I was taught this rule 30+ years ago and took it for granted however I have recognized a couple of textbooks that seem to state that unless otherwise noted consider the conductors as THW. Of course this may possibly change some of the way that I teach this, but I was wondering if this was noted in the NEC somewhere or used for uniformity in these tetbooks. I noticed Holt slides show this and an ATP text Electrical Systems based on the 2008 NEC.