As it's written, there are two ways to interpret 230.40, Exception 1. I suspect that don_resqcapt19 & ivsenroute are each interpreting it differently. The difference depends on whether the clause "run to each occupancy" modifies "service-entrance conductors" or "service." The sentence isn't clear. Here it is (parenthetical phrases omitted for clarity):
A building . . . shall be permitted to have one set of service-entrance conductors for each service, . . . run to each occupancy or group of occupancies.
If "run to each occupancy" modifies "service entrance conductors," it says that you can have multiple SECs (one set per occupancy) for each service. I think that this is don_resqcapt19's interpretation.
Alternatively, if "run to each occupancy" modifies "service," it says that you?re only permitted to have one set of SECs run to each occupancy . . . for each service to the building. I think that this is ivsenroute's interpretation.
Since it's an *exception* to the general rule stated before it, I think that there's little doubt that the authors intended it to mean that, under specified conditions, you could have multiple SECs branched off of a single drop or lateral. But that's not quite what it really says.