Small appliance circuits

Status
Not open for further replies.

chris1971

Senior Member
Location
Usa
Customer wants to have two receptacles installed above the kitchen cabinets to run some rope lighting. Can I tie onto the existing 20 amp small appliance branch circuits at the countertop? I couldn't find anything in the 08 NEC that would state otherwise?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Customer wants to have two receptacles installed above the kitchen cabinets to run some rope lighting. Can I tie onto the existing 20 amp small appliance branch circuits at the countertop? I couldn't find anything in the 08 NEC that would state otherwise?
No you may not. Look at 210.52(B)(2)
 